Biomass domestic boiler issue

rollestonpark

Member
Arable Farmer
Location
Burton on trent
So sounds like the kero boiler's heat does not go through the heat exchanger to get into the house heat network. It goes direct.
So probably the heat exchanger is too small, and/or there is insufficient flow of water through the heat exchanger on the house side (pump on slow setting or not big enough, on the house side)

We use a low loss header to exchange heat with the house, could try that... but this will mean the water in the biomass boiler and the house will become 1 and the same. (not an issue for us, but maybe for some)
 

mountfarm

Member
So sounds like the kero boiler's heat does not go through the heat exchanger to get into the house heat network. It goes direct.
So probably the heat exchanger is too small, and/or there is insufficient flow of water through the heat exchanger on the house side (pump on slow setting or not big enough, on the house side)

We use a low loss header to exchange heat with the house, could try that... but this will mean the water in the biomass boiler and the house will become 1 and the same. (not an issue for us, but maybe for some)

Yes correct the kero is not connected to the biomass. It’s stand alone deliberately due to the ofgem.

There’s a main pump in the biomass room 100m away. Not sure on size but it’s physically big. Took 4 blokes to lift it into place as it’s fixed about 6ft up in the air. Then there’s a booster pump in the house to ensure flow is maintained. This is a much smaller pump though. Again not sure the size off the top of my head but I’ll check tomorrow.
 

Frankzy

Member
Location
Jamtland, Sweden
if we put the motorised valve into manual then we get more heat in the house but then the return pipe is also red hot so we are sending heat back to the biomass boiler.

Seems pretty clear cut that the heat exchanger is not actually exchanging much heat..
We warm roughly 300m2 with 40 degree water and the hot side of the heat exchanger only needs to be around 60 to keep the house at 40.
 

mountfarm

Member
The original exchanger which is currently removed is Nordic Ba 32-20. This was temporarily replaced with a used Bowman 3705 3 GM just to try it as it’s much bigger. I don’t know the size but they are used in the marine industry and commonly found in swimming pools. The plumber suggested we try it. https://www.bowman-tr.com/en/u-marine-heat-exchangers_20.html
The plumber (didn’t fit the biomass system) has suggested today we run both of the above in line as the next trial.
 

mountfarm

Member
Seems pretty clear cut that the heat exchanger is not actually exchanging much heat..
We warm roughly 300m2 with 40 degree water and the hot side of the heat exchanger only needs to be around 60 to keep the house at 40.

The house is about 400sqm over 3 floors. It’s got double glazing which is new recently but it’s not properly insulated as there’s no cavity wall and the 3rd floor is bedrooms into the apex so no scope to run insulation as such.
 

rollestonpark

Member
Arable Farmer
Location
Burton on trent

mountfarm

Member

rollestonpark

Member
Arable Farmer
Location
Burton on trent
That looks OK... is it blocked inside in anyway?
is the pump working and big enough on the house side?
is there any valves or mixers working incorrectly and thus not allowing water to go through it properly...
 

wilber

Member
Location
wales
I know someone who's heat exchanger was flushed and they where shocked at the amount of sludge that had built up in. So maybe needs a clean?
 

Wisconsonian

Member
Trade
If this system worked before, and doesn't work now, then it's not a problem with the wrong heat exchanger. The plumber who suggested switching the heat exchangers, and now suggests putting them inline, has an advantage of having seen the system in person, but has still given bad advice. Get a different plumber, or heating person. If you don't know what is going on, putting them both inline is likely to reduce the flow and reduce the heat transfer. Unfortunately this is not a question for an internet forum, it takes someone measuring temperatures and figuring the flow of the system.
 

f0ster

Member
we find that heat exchangers require cleaned out from time to time, use hypoclorite but do not leave it in for more than a couple of hours, then pressure washer,
 

SFI - What % were you taking out of production?

  • 0 %

    Votes: 102 41.0%
  • Up to 25%

    Votes: 91 36.5%
  • 25-50%

    Votes: 37 14.9%
  • 50-75%

    Votes: 5 2.0%
  • 75-100%

    Votes: 3 1.2%
  • 100% I’ve had enough of farming!

    Votes: 11 4.4%

May Event: The most profitable farm diversification strategy 2024 - Mobile Data Centres

  • 916
  • 14
With just a internet connection and a plug socket you too can join over 70 farms currently earning up to £1.27 ppkw ~ 201% ROI

Register Here: https://www.eventbrite.com/e/the-mo...2024-mobile-data-centres-tickets-871045770347

Tuesday, May 21 · 10am - 2pm GMT+1

Location: Village Hotel Bury, Rochdale Road, Bury, BL9 7BQ

The Farming Forum has teamed up with the award winning hardware manufacturer Easy Compute to bring you an educational talk about how AI and blockchain technology is helping farmers to diversify their land.

Over the past 7 years, Easy Compute have been working with farmers, agricultural businesses, and renewable energy farms all across the UK to help turn leftover space into mini data centres. With...
Top