I wondered if anyone had used composite roofing on a class q recently, and if so what thickness was used please? It’s just for a re cladding of an existing building and was trying to future proof as much as possible. TIA.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Is this as part of an approved Class Q or for cladding a building with a future Class Q in mind?I wondered if anyone had used composite roofing on a class q recently, and if so what thickness was used please? It’s just for a re cladding of an existing building and was trying to future proof as much as possible. TIA.
Only cladding for it in mind for the future, I expect regs will change and we’ll be out of date anyway but thought it was worth thinking about.Is this as part of an approved Class Q or for cladding a building with a future Class Q in mind?
That's ok then, I have had people come to me after they replaced the roof panels as part of a Class Q conversion and Planning Enforcement had been informed. We had to apply for retrospective planning for the whole build just because of the extra 220mm height caused by the thicker panels.Only cladding for it in mind for the future, I expect regs will change and we’ll be out of date anyway but thought it was worth thinking about.
You can over clad existing roofs using a built up systemI wondered if anyone had used composite roofing on a class q recently, and if so what thickness was used please? It’s just for a re cladding of an existing building and was trying to future proof as much as possible. TIA.
Thank you, I was basing it on 80mm, so we’d be under spec anyway, do you know roughly what thickness the regs would equate to?You'd want to go as thick as possible really.
It's a bit complicated - for refurbishment of roofs the target u-value is 0.15W/m²K, but if it is 0.16W/m²K already then it can stay as is.
However a 80mm Briarwood panel has a u-value of 0.28W/m²K so you'd have to do some upgrading anyway. You can get thicker panels but there's space between the purlins that can be used to insulate.
Composite panels are non-fragile which helps a bit too.
A 120mm Kingspan KS1000RW has a u-value of 0.15.Thank you, I was basing it on 80mm, so we’d be under spec anyway, do you know roughly what thickness the regs would equate to?
I think you’re right, will just stick to 80mm and least it will be a good roof for other uses. Thank you for your reply.A 120mm Kingspan KS1000RW has a u-value of 0.15.
Although I would bother too much because in a conversion you'd need to put a ceiling up so adding some mineral wool in the depth of the purlin wouldn't be a major issue. So, worth comparing prices but if the Kingspan is too expensive then there's a get out down the road.
I put 150mm kingspan in the roof as they were cheaper than the 125mm that is obligatoryI think you’re right, will just stick to 80mm and least it will be a good roof for other uses. Thank you for your reply.