I have this fan from one of my walk in freezers.
  • On the bench with a 24v supply it runs.
  • The machine puts out 25-27v when appropriate (with motor disconnected)
  • The contacts of the motor connector make the continuity circuit buzz on the DMM (not sure if this is significant or not)
  • The contacts appear to present 0v when the motor is connected (and should be running)
Is this fixable?
Currently having trouble getting blades off due to a rusted set screw on the shaft. But if necessary I will persevere.
A new bare motor is £100 and a new whole assembly is £200.
 

Attachments

  • 20190502_122916.jpg
    20190502_122916.jpg
    256.5 KB · Views: 86

Greenbeast

Member
Location
East Sussex
Fridge engineer can't figure it out.
Fan runs off battery but not on unit.
Unit will run another fan

Apparently the circuit board load tests the fan and will cut out of too high (I think), whereas two car batteries will supply almost any current
 

milkloss

Member
Livestock Farmer
Location
East Sussex
Maybe wiz it down to deeprose, hollington road, Hastings. Don’t know if they’ve shutdown now so ring first. Genuine good old boys that know their stuff. Rewinds etc.
 

Greenbeast

Member
Location
East Sussex
Could it be the orientation? Maybe vertical in that machine and lies flat on the bench? Would mask a worn brush perhaps, if that were the case.

Interesting yes! I did lay it flay to test and it is vertical in the machine. Both brushes looked fine, although did sustain a tiny corner chip in each before they were put back :banghead: Is that enough to cause a problem?
I suppose i can borrow brushes from the working fan to test that
 

Fruitbat

Member
BASIS
Location
Worcestershire
The fans went in my cold store at the back end of last year, first one stopped, closely followed by the second as it was working it nuts off trying to move air through the now half frozen matrix. The grub screws holding the fan to the shaft were imperial hex and extremely tight, we had to resort to cutting the motor shaft and punching the stub through. Both motors still spun but as soon as power was turned on they would blow a fuse. Replacements off the shelf despite the cold store being over 30 years old...

ACRS, Pershore sorted me out
FB
 

milkloss

Member
Livestock Farmer
Location
East Sussex
Interesting yes! I did lay it flay to test and it is vertical in the machine. Both brushes looked fine, although did sustain a tiny corner chip in each before they were put back :banghead: Is that enough to cause a problem?
I suppose i can borrow brushes from the working fan to test that

Ah ha! Brushes you say. Try running a hacksaw or knife down the contact gaps on the commutator.
 

mogman

Member
Location
Cheshire
Is the motor dc?
I had a bit of trouble with some solenoids once got 24v on the tester and on a bulb but wouldn’t work the coil, it was a diode gone in the rectifyer so sending ac to the coil when it needed dc
 

Blue.

Member
Livestock Farmer
If you decide to give up and replace the motor I find the best way to get the fan off is cut the shaft off the motor,you can then punch it out in the vice without damaging the blades/hub.

Motor sounds lazy to me,replace with new.
 

Greenbeast

Member
Location
East Sussex
If you decide to give up and replace the motor I find the best way to get the fan off is cut the shaft off the motor,you can then punch it out in the vice without damaging the blades/hub.

Motor sounds lazy to me,replace with new.

I drilled out the set screw and hammered the shaft free. I may replace it yes, but at least I can do just the motor now instead of the whole thing.
 

SFI - What % were you taking out of production?

  • 0 %

    Votes: 103 40.6%
  • Up to 25%

    Votes: 93 36.6%
  • 25-50%

    Votes: 39 15.4%
  • 50-75%

    Votes: 5 2.0%
  • 75-100%

    Votes: 3 1.2%
  • 100% I’ve had enough of farming!

    Votes: 11 4.3%

May Event: The most profitable farm diversification strategy 2024 - Mobile Data Centres

  • 1,405
  • 26
With just a internet connection and a plug socket you too can join over 70 farms currently earning up to £1.27 ppkw ~ 201% ROI

Register Here: https://www.eventbrite.com/e/the-mo...2024-mobile-data-centres-tickets-871045770347

Tuesday, May 21 · 10am - 2pm GMT+1

Location: Village Hotel Bury, Rochdale Road, Bury, BL9 7BQ

The Farming Forum has teamed up with the award winning hardware manufacturer Easy Compute to bring you an educational talk about how AI and blockchain technology is helping farmers to diversify their land.

Over the past 7 years, Easy Compute have been working with farmers, agricultural businesses, and renewable energy farms all across the UK to help turn leftover space into mini data centres. With...
Top