Think pocket probe sensors measure heat not flow maybe ?Assume they have a propeller in pipe to measure flow?
If so I bet that’s blocked
Can you press buttons through sequences to clear ?It’s showing temperatures but no flow. It’s flashing “info” at the top which none of my others show ?
the meter cannot calculate the heat without the flow reading.Can you press buttons through sequences to clear ?
Do you need flow readings ?
RHI meter readings are just heat.
Was the pump running when you took the reading and if you have back end protection was it on bypass or full flow (depending on meter location)
Reading that sheet says the sum of multiple error codes is shown. So your '4112' will be a 4096 and a 16. I know no more.View attachment 722422
I’ve followed the instructions and can’t get any of the screens to display “error”
Take the cover off again and make sure you havn't bent one of the connector pins. Also disconnect the battery for a few seconds and put it back again.
https://able.co.uk/media/2015/01/kamstrup-402-iom.pdf
for my information, do you need to break the security seal to replace the batteries?
(just for when ours need doing)
Have you the reps contact details I may have it here ?I don’t think there was any seals on left hand side box with battery in. I’ve broken seal on right hand side thing and found water inside it. Replaced the circuit board inside it with a spare but still getting error so tomorrow I’m taking whole thing off and see if the water flow device is blocked