Powering a fan

Beefsmith

Member
We’ve a shed that next year will be used to store grain. It’s got single phase elec in it already for lights etc. We want to put a fan on the back to blowing grain. To get 3 phase we’ve got two options. The first is a 230m dig to install the cable from the nearest board. As the crow flies it’s only 100m but there’s sheds in the way so digging around them creates 230m.
Or a generator? Use would be obviously harvest time so August - September and then it’s sporadic for cooling so we are think no more than 3 months use per year in total but that could be between August and April. It’ll be a 37kw (50hp) fan.
 

Mur Huwcun

Member
Livestock Farmer
Location
North West Wales
Can’t you run the armoured cable through the sheds along rafters etc? Huge difference in voltage drop between 100m and 230 which I guess will more than double the size and cost of cable.
 

Beefsmith

Member
Hire companies might give a decent deal for 3 month hire
or SH 50 kva genny .
I`m guesing your 230 m cable will be well over £2000

£280/week so far is the best price and we will need a 150kva generator for a 37kw fan according to a local sparky. He said anything less wont start the fan up.
 

Beefsmith

Member
Can’t you run the armoured cable through the sheds along rafters etc? Huge difference in voltage drop between 100m and 230 which I guess will more than double the size and cost of cable.

The sheds are all units and walled to the apex so it would mean cutting through bricks and plasterboard as they are offices.
 

Blue.

Member
Livestock Farmer
35mm2 4 core would be about £10/m

Good for over 40kw.

As posted get a 2nd opinion,most sparks go way over the top on these type of things.
 
run a pair of 25 hp start them up one after the other fit a baffle door in the tunnel to stop the back pressure then when both up to speed open the door ,,, takes so much off the start up load ,, think from memory start up is 3 times the run amps as stated on the motor

Yup I’d agree there. Soft start \ more fans and controls means you can call for the power slowly thus not needing such a big supply
 

TheTallGuy

Member
Location
Cambridgeshire
run a pair of 25 hp start them up one after the other fit a baffle door in the tunnel to stop the back pressure then when both up to speed open the door ,,, takes so much off the start up load ,, think from memory start up is 3 times the run amps as stated on the motor
The multiplier factor will depend on motor spec & when running on a genny it will depend on the generator controls/overload control. I have a 5kVA genny that won't start one 650W motor, but will run a 2kW vacuum cleaner motor!
 

Badshot

Member
Location
Kent
Defo use two fans, then if you only use part of the store you only need one fan. And for cooling as well.
You'll need soft starts not star deltas.
Maybe look into the variable run ones so you can reduce the high speed running too if it's not necessary to run flat out.
 

Deutzdx3

Member
Use an inverter if the power supply allows. We run a 10hp screw compressor off one and 2 3kw motors powering a spray booth. Been doing it for 10 years hostel free. Just need the right size cabling and power supply.
 

SFI - What % were you taking out of production?

  • 0 %

    Votes: 113 38.4%
  • Up to 25%

    Votes: 112 38.1%
  • 25-50%

    Votes: 42 14.3%
  • 50-75%

    Votes: 6 2.0%
  • 75-100%

    Votes: 4 1.4%
  • 100% I’ve had enough of farming!

    Votes: 17 5.8%

May Event: The most profitable farm diversification strategy 2024 - Mobile Data Centres

  • 3,815
  • 59
With just a internet connection and a plug socket you too can join over 70 farms currently earning up to £1.27 ppkw ~ 201% ROI

Register Here: https://www.eventbrite.com/e/the-mo...2024-mobile-data-centres-tickets-871045770347

Tuesday, May 21 · 10am - 2pm GMT+1

Location: Village Hotel Bury, Rochdale Road, Bury, BL9 7BQ

The Farming Forum has teamed up with the award winning hardware manufacturer Easy Compute to bring you an educational talk about how AI and blockchain technology is helping farmers to diversify their land.

Over the past 7 years, Easy Compute have been working with farmers, agricultural businesses, and renewable energy farms all across the UK to help turn leftover space into mini data centres. With...
Top