Earth cable size on three phase

milkloss

Member
Livestock Farmer
Location
East Sussex
When I looked into this it got complicated as it depends on your earthing system. A tt (earthrod) for a 100amp 3ph supply needs to have 16mm2 earth for up to 35mm2 incoming tail size if not mechanically protected, I think it can be much smaller if protected but both answers should be calculated depending on earth rod resistance etc etc.

I’m no leccy so I advise professional opinion but we used a 16mm earth.
 

Pond digger

Never Forgotten
Honorary Member
Location
East Yorkshire
When I looked into this it got complicated as it depends on your earthing system. A tt (earthrod) for a 100amp 3ph supply needs to have 16mm2 earth for up to 35mm2 incoming tail size if not mechanically protected, I think it can be much smaller if protected but both answers should be calculated depending on earth rod resistance etc etc.

I’m no leccy so I advise professional opinion but we used a 16mm earth.

Sorry, I should’ve been more specific: I’m leaving the complicated stuff to an electrician. I was meaning wires in 3phase machine isolators, sockets etc. Most stuff that I have will be fed by 2.5mm2 wire: I was just wondering if the earth wire is ok at the same size, or should you perhaps use 4mm2 for the earth.

Interesting what your saying about main earthing though. I have three phase already, and am taking power from a 63amp fused (32amp) isolator switch via armoured cable to a new distribution board about 15 m from where the main incoming feed is situated. The armoured cable is 4 core 10mm2. Ive been reading a bit about the earthing capacity of the steel armour and the conductive deficiency of steel in comparison to copper: but as said, I’ll be leaving that one for the electrician.
 

milkloss

Member
Livestock Farmer
Location
East Sussex
Sorry, I should’ve been more specific: I’m leaving the complicated stuff to an electrician. I was meaning wires in 3phase machine isolators, sockets etc. Most stuff that I have will be fed by 2.5mm2 wire: I was just wondering if the earth wire is ok at the same size, or should you perhaps use 4mm2 for the earth.

Interesting what your saying about main earthing though. I have three phase already, and am taking power from a 63amp fused (32amp) isolator switch via armoured cable to a new distribution board about 15 m from where the main incoming feed is situated. The armoured cable is 4 core 10mm2. Ive been reading a bit about the earthing capacity of the steel armour and the conductive deficiency of steel in comparison to copper: but as said, I’ll be leaving that one for the electrician.

It’ll be fine the same size I expect. It might be that it doesn’t have to be as big as the lives but to save argument I’d go equivalent.

Anything I run now doesn’t use the armour as earthing, much easier to buy 5 core than worry about getting the glands spot on etc. It’s still terminated and earthed as best can be done but I’ve seen enough shaky gland connections to metal isolator boxes to give me the willies!
 

Pond digger

Never Forgotten
Honorary Member
Location
East Yorkshire
It’ll be fine the same size I expect. It might be that it doesn’t have to be as big as the lives but to save argument I’d go equivalent.

Anything I run now doesn’t use the armour as earthing, much easier to buy 5 core than worry about getting the glands spot on etc. It’s still terminated and earthed as best can be done but I’ve seen enough shaky gland connections to metal isolator boxes to give me the willies!

Thanks

I actually quite enjoy fitting glands. I wish I knew more about the technical side of this electrickery stuff, I mean mcb class b, c, and d :scratchhead:. Can’t beat a bit of fuse wire I say:rolleyes:. But seriously, most of the job just entails screwing stuff to walls and making terminal connection, which I find really satisfying.
 

Netherfield

Member
Location
West Yorkshire
You will find in Twin and earth cable that the earth is of a smaller diameter, and that technically the neutral does not need to be a big as the live, a three phase board can use the three live wires and just the one neutral for return. And many years ago the electricity companies used to use what was known as a three and a half core cable, where the neutral was only half size of the lives.
 

jamj

Member
Location
Down
It is frowned on now to use armour as the earth.
Not sure if regs permit it or not, but I would use 5 core as mentioned above.
As for size, if you are fitting surge protection then larger earth size is needed. Current takes easiest path and that will be down wire/path with least resistance.
 

Pond digger

Never Forgotten
Honorary Member
Location
East Yorkshire
It is frowned on now to use armour as the earth.
Not sure if regs permit it or not, but I would use 5 core as mentioned above.
As for size, if you are fitting surge protection then larger earth size is needed. Current takes easiest path and that will be down wire/path with least resistance.
Bit late to be suggesting 5 core I’m afraid. They still sell 4 core armoured so can’t imagine it’s not permitted to use the armour for earthing. I’ll see what the electrician says when he comes to check things out, but the issue has never been raised previously.
 

SFI - What % were you taking out of production?

  • 0 %

    Votes: 105 40.5%
  • Up to 25%

    Votes: 94 36.3%
  • 25-50%

    Votes: 39 15.1%
  • 50-75%

    Votes: 5 1.9%
  • 75-100%

    Votes: 3 1.2%
  • 100% I’ve had enough of farming!

    Votes: 13 5.0%

May Event: The most profitable farm diversification strategy 2024 - Mobile Data Centres

  • 1,735
  • 32
With just a internet connection and a plug socket you too can join over 70 farms currently earning up to £1.27 ppkw ~ 201% ROI

Register Here: https://www.eventbrite.com/e/the-mo...2024-mobile-data-centres-tickets-871045770347

Tuesday, May 21 · 10am - 2pm GMT+1

Location: Village Hotel Bury, Rochdale Road, Bury, BL9 7BQ

The Farming Forum has teamed up with the award winning hardware manufacturer Easy Compute to bring you an educational talk about how AI and blockchain technology is helping farmers to diversify their land.

Over the past 7 years, Easy Compute have been working with farmers, agricultural businesses, and renewable energy farms all across the UK to help turn leftover space into mini data centres. With...
Top