Its 240v supply ,then inverter to a 3phase motor
It would need to be overated by that much.And has Servac has mentioned, the part number is for a 12kw inverter, but you only have a 4.0kw motor, so vastly oversized.
It would need to be overated by that much.
My brother wired it in ,hes a electrician but hes never came across an inverter,
He followed the wire diagram, so i think its wired in correct,but we couldnt figure out the all the settings,
It automatically seemed to sort itself out and we just press start and it goes.
It says on the read out f50.00 which we didn't set up.does this mean the hz?as the motor is 50hz.
Is there a way to check if the motor is running at the correct rpm?
It could also be the way i have the ducting off the extractor set up but i wanted to eliminate a slow running motor / fault with inverter.
You could buy a tacho off ebay and measure the speed? Non contact or contact type cheap enough off ebay.
Can you put up pictures of the motor rating plate and of the motor terminals and find out what the following parameters are set to Input AC supply voltage
Maximum output frequency
Maximum outout voltage
Base Frequency
Motor rated current
Motor pole count
Motor rated power
Unless you can check/change thease things you have little hope of getting it working properly.
3 phase is normally 400v which is how the motor has been wired to run, but when you run an inverter from a 230v single phase supply you get 230v 3phase out, which means that the motor would only run at 2/3 of its rated power. By rewiring to delta it will run on 230v 3 phase at its full power rating.Ah cheers!
Will get brother to do it tonight,
So is the way the motor is wired currently is star?
What is the issue with it wired as it currently is, is it that the motor will run slower?
I dont know alot about this sort of stuff ,
It be good to understand the reasons why its incorrect.
Cheers again for help!
That is the correct inverter for single phase in. As Servac said, wire the motor in delta and you'll be good to go. There will be two of these connector bars on top of each other in the current wiring, just incase you think you don't have enough.I will have a look later on today and get my brother to confirm if it is delta,
here is all the info on the inverter
View attachment 940275View attachment 940276View attachment 940274
Cheers for all the help so far