fire proof walling for commercial units

Location
somerset
splitting up some agricultural buildings into commercial units. The partition walls should be fire proof to withstand 1 hr, what are people using was thinking of precast concrete panels you can get fireproof composite panels but cant push against them any ideas would be helpful
 
Unless you get a written guarantee off your panel supplier building control will not sign off concrete panels as a firewall partition. Currently doing a 4 building site where this has happened and the panel order has been cancelled and now the partitions are being clad to floor level.

Twin skin block wall if you need to be able to push against them, unless you are just pushing 1 side then you could just clad the back side of the concrete panels.
 

robs1

Member
Unless you get a written guarantee off your panel supplier building control will not sign off concrete panels as a firewall partition. Currently doing a 4 building site where this has happened and the panel order has been cancelled and now the partitions are being clad to floor level.

Twin skin block wall if you need to be able to push against them, unless you are just pushing 1 side then you could just clad the back side of the concrete panels.
What are they cladding with that is permissible as a fire wall?
 

Doing it for the kids

Member
Arable Farmer
We did a stud wall and double plasterboard on both sides with Rock wool between to separate boiler house from next door.

Didn’t ask for nor request feedback from the officials over it but plasterboard is hard to burn!

Can also get fire board that’s like thin flat fibre cement sheets
 

The Arable Farmer

Member
Arable Farmer
Unless you get a written guarantee off your panel supplier building control will not sign off concrete panels as a firewall partition. Currently doing a 4 building site where this has happened and the panel order has been cancelled and now the partitions are being clad to floor level.

Twin skin block wall if you need to be able to push against them, unless you are just pushing 1 side then you could just clad the back side of the concrete panels.
Is this being clad with composite panels or built up white liner sheets with insulation rolled between?
 

flinty123

Member
Mixed Farmer
Have building control said anything about the steel purlins needing treating with intumescent paint, as they cross over into the neighbouring unit, through the party wall?
 

flinty123

Member
Mixed Farmer
Good question that.

I had to paint steel columns between units with intumescent paint but that was all.

They have asked us to paint the purlins with intumescent paint. The building inspector said a minimum of 1.5m either side of the party wall to prevent fire spread, seems a bit overkill, but he is adamant it is needed unfortunately.
 
What are they cladding with that is permissible as a fire wall?

Yes composite panel being used to the floor level now. This can be a freestanding wall panel that sits on the floor, or a standard composite panel fixed to cold rolled rails etc, if its a retrofit and you dont have internal columns then the freestanding ones are a good option.

You can single skin both sides of the cold rolled rails but you need to fill it with fireproof rockwool and also use firetape on the rail faces etc


They have asked us to paint the purlins with intumescent paint. The building inspector said a minimum of 1.5m either side of the party wall to prevent fire spread, seems a bit overkill, but he is adamant it is needed unfortunately.

Never heard of them asking for cold rolled to be painted.

Look out for the roof light positions when roof is laid, they cannot be within 1500mm of the partition either
 

flinty123

Member
Mixed Farmer
Yes composite panel being used to the floor level now. This can be a freestanding wall panel that sits on the floor, or a standard composite panel fixed to cold rolled rails etc, if its a retrofit and you dont have internal columns then the freestanding ones are a good option.

You can single skin both sides of the cold rolled rails but you need to fill it with fireproof rockwool and also use firetape on the rail faces etc




Never heard of them asking for cold rolled to be painted.

Look out for the roof light positions when roof is laid, they cannot be within 1500mm of the partition either
 

Attachments

  • Screenshot_20240327-202840_Samsung Notes.jpg
    Screenshot_20240327-202840_Samsung Notes.jpg
    186.6 KB · Views: 0

The Arable Farmer

Member
Arable Farmer
Yes composite panel being used to the floor level now. This can be a freestanding wall panel that sits on the floor, or a standard composite panel fixed to cold rolled rails etc, if its a retrofit and you dont have internal columns then the freestanding ones are a good option.

You can single skin both sides of the cold rolled rails but you need to fill it with fireproof rockwool and also use firetape on the rail faces etc




Never heard of them asking for cold rolled to be painted.

Look out for the roof light positions when roof is laid, they cannot be within 1500mm of the partition either
What composite panels are they? Would a normal kingspan ks1000rw do the trick? Could you solid block up to say 2m then panel above to roofline?
 
I believe its the 80mm ks1000 panel you need to get +60mins fire integrity, but worth asking kingspan before ordering.

Intumescent paint will depend on the use/location/ownership etc
 
Tags
fire

Will you help clear snow?

  • yes

    Votes: 68 32.1%
  • no

    Votes: 144 67.9%