How many MW's can a 133KVA line carry!?

Its not as simple as that, I know and so many factors depend on the answer.

But, are we talking, 200 MW, 2000 MW or 20,000 MW!?

TYIA

I assume you mean how many megawatts can a 132 kV line carry? This would be the standard voltage in the UK which is considered transmission level in Scotland and distribution level in England.

As you've observed, it's virtually impossible to give a proper answer since there are so many variables. As a VERY rough guestimate, 1000 amps per phase at 132kV works out at around 230MW. However, there are many factors involved, such as:
  • Is it overhead or underground?
  • Is it winter or summer?
  • What size are the conductors?
  • How long is it?
  • What size transformer is at either end? What is the busbar arrangement?
  • What are the protection considerations? What is the fault level?
  • What are the reactive power limitations?
I don't recall the exact value, but National Grid will not allow more generation to be connected to any one set of towers than they have backup diesel capacity. The theory being they could never allow one pylon to fall down and take out more generation than they could rapidly replace. I believe that number was 2GW at one point but I can't recall accurately.
 
I assume you mean how many megawatts can a 132 kV line carry? This would be the standard voltage in the UK which is considered transmission level in Scotland and distribution level in England.

As you've observed, it's virtually impossible to give a proper answer since there are so many variables. As a VERY rough guestimate, 1000 amps per phase at 132kV works out at around 230MW. However, there are many factors involved, such as:
  • Is it overhead or underground?
  • Is it winter or summer?
  • What size are the conductors?
  • How long is it?
  • What size transformer is at either end? What is the busbar arrangement?
  • What are the protection considerations? What is the fault level?
  • What are the reactive power limitations?
I don't recall the exact value, but National Grid will not allow more generation to be connected to any one set of towers than they have backup diesel capacity. The theory being they could never allow one pylon to fall down and take out more generation than they could rapidly replace. I believe that number was 2GW at one point but I can't recall accurately.

Thanks

yup 132 KVA was what I meant.

When you say 230 MW, is this per Tower or per side of Tower. Assuming per Tower?
 

Exfarmer

Member
Location
Bury St Edmunds
It depends on the number of lines and the size of the lines.
so the towers will carry 3 layers of lines.
this is the three phases
the lines will often be in groups of 4 on each side of the Tower per layer, maybe more.
It is then how much each Line can carry amperage wise that counts.
a wire can carry so many amps irrespective of voltage. The longer the line, the greater the amps, the greater the voltage drop and the greater the heat build up in the line.
as heat builds up, the greater the voltage loss.
so the longer the line, ie. North of Scotland to South of England the more the loss in voltage and so less amperage which can be pushed through it
 
IMG_3926.jpg


thanks all. I think I have enough info now to confirm what I suspected :)
 
Near us the lines originally installed in the early 60's have been re-strung with groups of 3 instead of groups of 4 but when we enquired we were told that the newer 3 grouping could actually carry a higher current than the older 4's.
 

fermerboy

Member
Location
Banffshire
We have had the towers through us re strung with wire twice as thick and voltage ramped to 275Kv to get the power moved South. And they are now on about going to 400kv!!!
We are next to the UKs largest substation and second biggest substation in Europe though, and I'm led to believe the only one in the world with 11kv, 33kv, 132kv, 275kv, 400kv on one site. Thats not counting the ordinary 415 and 240v!!!
 
Last edited:

SFI - What % were you taking out of production?

  • 0 %

    Votes: 105 40.9%
  • Up to 25%

    Votes: 93 36.2%
  • 25-50%

    Votes: 39 15.2%
  • 50-75%

    Votes: 5 1.9%
  • 75-100%

    Votes: 3 1.2%
  • 100% I’ve had enough of farming!

    Votes: 12 4.7%

May Event: The most profitable farm diversification strategy 2024 - Mobile Data Centres

  • 1,702
  • 32
With just a internet connection and a plug socket you too can join over 70 farms currently earning up to £1.27 ppkw ~ 201% ROI

Register Here: https://www.eventbrite.com/e/the-mo...2024-mobile-data-centres-tickets-871045770347

Tuesday, May 21 · 10am - 2pm GMT+1

Location: Village Hotel Bury, Rochdale Road, Bury, BL9 7BQ

The Farming Forum has teamed up with the award winning hardware manufacturer Easy Compute to bring you an educational talk about how AI and blockchain technology is helping farmers to diversify their land.

Over the past 7 years, Easy Compute have been working with farmers, agricultural businesses, and renewable energy farms all across the UK to help turn leftover space into mini data centres. With...
Top