anyone had issues with this. I am starting to have issues on one site, we are currently having board investigate, but the feed back from their personell doing the investigation does not sound good
They appear to be blaming me for putting too much into the grid.
Obviously I am not feeding any more since we placed the install 5 years ago .
3 years ago a neighbour was given permission to 30 kw install solar on his roof and we believe issues started then.
We have had inverters failing at odd times since, 2 out of 5 replaced under warrantty .
During a routine inspection on the 2nd. Of this month, I noticed the inverters were going ape every time the sun came out, it was one of thise days with a lot of cloud but odd clearing and a lot of sun then.
As the sun came out the inverters would immediately rise to about 40kw production when at least one and several times up to 3 dropped out.
After 2 or 3 minutes they came back in. Production then as soon as all five cut in immediately 2 or 3 would drop out again.
They were all reading over voltage.
In fact they have given readings of up to 507 volts ( 3 phase)
The board man who saw this horrified! Anything over 460 apparently is a complete no no.
They are currently monitoring the line voltage, but as said before they were suggesting we need to change, or reduce our equipment,any one else had this problem
The panels feed chicken sheds, i believe the issue was created by both the sheds our panels are on and the other sheds, again poultry, were empty meaning consumption was near zero, due to the cycles of production coming together, which does not happen regularly.
I would appreciate any comments from anyone else who has had this issue, whether publicly or private.
They appear to be blaming me for putting too much into the grid.
Obviously I am not feeding any more since we placed the install 5 years ago .
3 years ago a neighbour was given permission to 30 kw install solar on his roof and we believe issues started then.
We have had inverters failing at odd times since, 2 out of 5 replaced under warrantty .
During a routine inspection on the 2nd. Of this month, I noticed the inverters were going ape every time the sun came out, it was one of thise days with a lot of cloud but odd clearing and a lot of sun then.
As the sun came out the inverters would immediately rise to about 40kw production when at least one and several times up to 3 dropped out.
After 2 or 3 minutes they came back in. Production then as soon as all five cut in immediately 2 or 3 would drop out again.
They were all reading over voltage.
In fact they have given readings of up to 507 volts ( 3 phase)
The board man who saw this horrified! Anything over 460 apparently is a complete no no.
They are currently monitoring the line voltage, but as said before they were suggesting we need to change, or reduce our equipment,any one else had this problem
The panels feed chicken sheds, i believe the issue was created by both the sheds our panels are on and the other sheds, again poultry, were empty meaning consumption was near zero, due to the cycles of production coming together, which does not happen regularly.
I would appreciate any comments from anyone else who has had this issue, whether publicly or private.