Buffer tank for biomass boiler

f0ster

Member
to regulate the heat output from the boiler is not always easy, depending on the boiler type you not only have to regulate the chip feed rate but also the primary and secondary fan speeds to match the feed rate. and also you really need the flame temp to be well up above 600 deg, 700deg is quite often the upper limit to make the boiler last longer. with heat exchangers you size them according to what you want it to do, for example to get instant hot water without the need for a hot water tank it required quite a large plate area because you are taking cold water to 60 deg within seconds, where for a house heating system it can be a lot smaller because it can circulate many times to build up the heat. you do not have to always use a PHE, it just makes it easier for working on the system and less damage done if you get a leak somewhere. there is only so much water you can pass through a given size of pipe without creating cavitation.
 

f0ster

Member
it might work ok, we had four 200kw froling boilers heating four large radiators/fans, one rad each. the mixer was starting to open the bypass because the return temp was hovering at about 50 deg
 

Bloders

Member
Location
Ruabon
expansion vessel will need to be in the order of 4% of system volume - dont underestimate how big they need to be
second point, dont underestimate how expensive it can be to insulate a buffer tank.
as usual, we did ours on the cheap, but to do it the "regular" way would have cost about 2K in insulation, plus the labour of fitting it. Saying that though, its very good stuff - water can be at 80 degress inside and you cannot detect a temperature tise on the outside.
 

strawman

New Member
We have three 999kwh boilers each with a 100m3 buffer tank. These are available second-hand from glasshouse companies in Holland. Expensive option but well worth it as the boilers are kept working all the day and night. Biomass boilers are better run on a constant load
 

Bernt

Member
No buffers on a log boiler!!!!!!! and no expansion vessel on a sealed system - i'd be reporting your installer and get it done properly, just a matter of time till you post that your pipework has burst and blown your house up!!!!!!! Also most reputable biomass boiler manufacturers state expansion should be 10% of system volume. 5% is currently recommended by CIBSE for domestic and small scale heating systems.
 

How is your SFI 24 application progressing?

  • havn't been invited to apply

    Votes: 30 34.5%
  • have been invited to apply

    Votes: 17 19.5%
  • applied but not yet accepted

    Votes: 29 33.3%
  • agreement up and running

    Votes: 11 12.6%

Webinar: Expanded Sustainable Farming Incentive offer 2024 -26th Sept

  • 2,564
  • 50
On Thursday 26th September, we’re holding a webinar for farmers to go through the guidance, actions and detail for the expanded Sustainable Farming Incentive (SFI) offer. This was planned for end of May, but had to be delayed due to the general election. We apologise about that.

Farming and Countryside Programme Director, Janet Hughes will be joined by policy leads working on SFI, and colleagues from the Rural Payment Agency and Catchment Sensitive Farming.

This webinar will be...
Back
Top