- Boroughbridge, york
One out of 3 pumps running now, frustratingly other two have some master/slave connection issues, the manufacturer need to come and sort that out .
On the plus side the one pump has lifted the house temp from 8 C to 25C in 18 hours, incoming air temp is approx 45C blowing 5000 cubic m/hour
The glycol in the ground loop leaves the pump at -1.5C and returns at 8C
Ill have to fire the gas heaters up to reach shed full temperature before Fri morning when the birds arrive
no photos as there is nothing to see, just a white box humming.
On the plus side the one pump has lifted the house temp from 8 C to 25C in 18 hours, incoming air temp is approx 45C blowing 5000 cubic m/hour
The glycol in the ground loop leaves the pump at -1.5C and returns at 8C
Ill have to fire the gas heaters up to reach shed full temperature before Fri morning when the birds arrive
no photos as there is nothing to see, just a white box humming.